> For the complete documentation index, see [llms.txt](https://doc.realvirtual.io/llms.txt). Markdown versions of documentation pages are available by appending `.md` to page URLs; this page is available as [Markdown](https://doc.realvirtual.io/components-and-scripts/interfaces/ethernetip.md).

# EthernetIP (Pro)

Connecting Allen-Bradley, Omron, Schneider Electric and other EtherNet/IP compatible PLCs with realvirtual.io for industrial automation and virtual commissioning

{% hint style="warning" %}
EthernetIP interface is only included in realvirtual.io Professional
{% endhint %}

## Overview

The EtherNet/IP interface enables direct communication between realvirtual.io and industrial controllers using the Common Industrial Protocol (CIP) over standard Ethernet networks. EtherNet/IP (Industrial Protocol) is one of the leading industrial communication protocols in North America and is widely adopted across manufacturing, process control, and hybrid automation systems.

This interface provides seamless integration with major PLC manufacturers including Allen-Bradley (Rockwell Automation), Omron, and Schneider Electric controllers, enabling true virtual commissioning workflows where your Unity simulation communicates directly with real industrial hardware.

**Key Features:**

* Direct tag-based communication with Allen-Bradley ControlLogix, CompactLogix, and MicroLogix systems
* Support for Omron NJ/NX series and Schneider Electric Modicon controllers
* Real-time bidirectional data exchange with sub-100ms cycle times
* Bulk signal import from CSV files exported from programming software
* Built-in connection diagnostics and error handling
* Thread-safe communication architecture for production environments

## Properties

The EtherNet/IP interface requires configuration of network settings and communication parameters through the Unity Inspector:

<figure><img src="https://260262196-files.gitbook.io/~/files/v0/b/gitbook-x-prod.appspot.com/o/spaces%2FpYxFg97YnJX96UzNNTSd%2Fuploads%2Fgit-blob-526b1cb05f60a643ffe673f2d6a26d3a20b70e2f%2Fethernetip-interface-inspector.png?alt=media" alt="EthernetIP Interface Inspector showing all configuration properties and buttons"><figcaption><p>EthernetIP Interface component in Unity Inspector with all configuration properties</p></figcaption></figure>

**IP-Address** (string) The IP address or hostname of the target PLC or EtherNet/IP gateway device. Include optional port number using colon notation (e.g., `192.168.1.100:44819`). Standard EtherNet/IP uses port 44818, but some configurations may require different ports. Must be accessible from the Unity application's network segment.

**Path** (string) CIP routing path specifying the physical location of the target controller within the chassis or backplane. For Allen-Bradley ControlLogix/CompactLogix systems, typical values are `1,0` (backplane position 1, slot 0) or `1,2` (backplane position 1, slot 2). For Logix systems communicating through DH+ bridges, this path defines the routing through multiple network segments. Leave empty for Micro800 series controllers which do not require routing paths.

**PLCType** (enum) Controller family selection that optimizes communication protocol behavior for specific PLC architectures. Available options include:

* **controllogix**: Allen-Bradley ControlLogix and CompactLogix systems (recommended for most Rockwell applications)
* **micro800**: Allen-Bradley Micro800 series controllers
* **slc500**: Allen-Bradley SLC 500 family PLCs
* **plc5**: Legacy Allen-Bradley PLC-5 systems
* **omron-njnx**: Omron NJ and NX series controllers

**Protocol** (enum) Communication protocol selection determining the network-level protocol used for data exchange:

* **ab\_eip**: Allen-Bradley EtherNet/IP protocol (recommended for Rockwell and compatible systems)
* **modbus-tcp**: Modbus TCP protocol for broader industrial device compatibility

**Debug Mode** (boolean) Enables additional logging of communication operations to the Unity Console. When enabled, outputs signal initialization status, connection errors, and signal operation details. Useful for troubleshooting connection issues and verifying signal setup. Disable in production environments to reduce console log volume.

**Timeout** (integer) Communication timeout value in milliseconds for individual tag operations. Higher values provide more tolerance for network latency and PLC response delays but reduce overall system responsiveness. Typical range: 1000-10000ms depending on network conditions and controller performance.

**PLCSignalTable** (string) File path to CSV-format signal definition table for bulk signal import. Use the "Select PLC Signal table" button in the Inspector to browse for CSV files exported from programming software like RSLogix 5000/Studio 5000. After selecting a file, click "Import PLC signal table" to automatically create Signal GameObjects. File must follow specific column format: Symbol, Direction (INPUT/OUTPUT), Type, Comment.

**UpdateCycle** (read-only) Current communication cycle counter that increments with each successful read/write operation cycle. Provides real-time indication of communication activity and connection health. Value resets to 0 when the interface reconnects or is restarted.

**Thread Status** (read-only) Displays the current status of the communication thread that handles PLC data exchange. Shows whether the background thread is running, stopped, or experiencing errors. This status indicates the health of the parallel communication system that ensures non-blocking Unity performance.

**Test Connect** (button) Tests the current configuration by attempting to connect to the specified PLC. Displays connection results in Unity Console.

**Select PLC Signal table** (button) Opens file browser to select CSV file containing signal definitions for bulk import.

**Import PLC signal table** (button) Processes the selected CSV file and creates Signal child GameObjects automatically.

## PLC Configuration

### Allen-Bradley ControlLogix/CompactLogix Setup

For Allen-Bradley controllers, ensure the following configuration in RSLogix 5000/Studio 5000:

1. **Network Configuration**: Configure the Ethernet module with a static IP address accessible from your Unity application
2. **Tag Creation**: Create controller-scoped tags or program-scoped tags that will be accessed from realvirtual.io
3. **Data Types**: Use supported data types (REAL, BOOL, INT, SINT, DINT) for optimal compatibility
4. **Security**: Ensure the controller's security settings allow external read/write access

**Example Tag Naming Conventions:**

* Controller tags: `ConveyorSpeed`, `SystemEnabled`, `ProductCount`
* Program tags: `Program:MainSequence.StepNumber`, `Program:Safety.EmergencyStop`
* Array elements: `ProductData[0]`, `AxisPosition[3]`

### Omron NJ/NX Series Setup

For Omron controllers using Sysmac Studio:

1. **EtherNet/IP Configuration**: Enable EtherNet/IP adapter functionality in the network configuration
2. **Tag Definition**: Create global variables with appropriate data types
3. **Network Settings**: Configure built-in EtherNet/IP port with static IP addressing

### Micro800 Configuration

Micro800 series controllers require simplified configuration:

1. **Ethernet Configuration**: Set static IP address in Connected Components Workbench
2. **Path Setting**: Leave the Path field empty in realvirtual.io Inspector
3. **Tag Access**: Use simple tag names without program qualifiers

## Signal Configuration

### Manual Signal Setup

Signals can be created manually for precise control over tag mapping and configuration. This is useful when you need to connect to specific PLC tags without importing an entire signal table.

#### Creating Signals Manually

1. **Create Child GameObject**: Right-click the EtherNet/IP interface GameObject and create an empty child GameObject
2. **Add Signal Component**: Add the appropriate PLCInput or PLCOutput component based on data flow:
   * **PLCInputBool/Int/Float**: Data flows FROM Unity TO PLC (Unity → PLC) - PLC Input from PLC perspective
   * **PLCOutputBool/Int/Float**: Data flows FROM PLC TO Unity (PLC → Unity) - PLC Output from PLC perspective
3. **Configure Signal Properties**:
   * **Name**: Enter the exact PLC tag name (e.g., `ConveyorSpeed`, `Program:MainSequence.StepNumber`)
   * **Comment**: Optional description for documentation
   * **OriginDataType**: Specify the exact PLC data type (critical for proper communication)

#### OriginDataType Configuration

The **OriginDataType** field tells the interface how to interpret the data at the PLC level. This is crucial for correct data conversion between PLC and Unity.

**When to Set OriginDataType:**

* **Always required** when creating signals manually
* **Automatically set** when importing from CSV or PLC discovery
* Must match the exact data type defined in your PLC program

**Common OriginDataType Values:**

| OriginDataType | PLC Data Type         | realvirtual Signal Type      | Description                     |
| -------------- | --------------------- | ---------------------------- | ------------------------------- |
| BOOL           | Boolean               | PLCInputBool/PLCOutputBool   | Single bit (true/false)         |
| SINT           | 8-bit signed integer  | PLCInputInt/PLCOutputInt     | -128 to 127                     |
| INT            | 16-bit signed integer | PLCInputInt/PLCOutputInt     | -32,768 to 32,767               |
| DINT           | 32-bit signed integer | PLCInputInt/PLCOutputInt     | -2,147,483,648 to 2,147,483,647 |
| REAL           | 32-bit floating point | PLCInputFloat/PLCOutputFloat | IEEE 754 single precision       |

#### Important Notes for Manual Configuration

* **Tag Name Must Match Exactly**: The Name field must match the PLC tag name exactly, including case sensitivity
* **Data Type Mapping**: Multiple PLC integer types (SINT, INT, DINT) all map to PLCInputInt/PLCOutputInt in realvirtual
* **Boolean Outputs**: Due to EtherNet/IP protocol limitations, boolean outputs may use SINT in the PLC
* **Array Access**: Include array indices directly in the Name field using standard Allen-Bradley syntax (e.g., `ProductData[0]`, `Matrix[2,5]`)
* **Verification**: Use Debug Mode to verify successful tag connection after starting play mode

### Automatic Signal Import

#### CSV Signal Import

For bulk signal configuration, create a CSV file with the following format:

**CSV File Format:**

```
Symbol,Direction,Type,Comment
ConveyorSpeed,INPUT,REAL,Main conveyor belt speed in m/min
SystemStart,OUTPUT,BOOL,System start command from operator
ProductCount,INPUT,DINT,Total products processed today
EmergencyStop,INPUT,BOOL,Safety system emergency stop status
```

**CSV Import Process:**

1. Export tag list from your programming software (RSLogix, Sysmac Studio, etc.)
2. Format according to required column structure
3. Use "Select PLC Signal table" button in the Inspector to browse for the CSV file
4. Click "Import PLC signal table" to automatically create Signal GameObjects (existing signals with matching names are preserved)

**CSV Requirements:**

* No header row in the CSV file
* Column order: Symbol, Direction (INPUT/OUTPUT), Type, Comment
* Type must exactly match supported data types: REAL, BOOL, INT, SINT, DINT
* Symbol must match exact tag names in PLC program including case sensitivity

## Data Types

The EtherNet/IP interface supports the following data type mappings between PLC tags and realvirtual.io signals:

| PLC Data Type | realvirtual Signal Type        | Description                | Value Range                     |
| ------------- | ------------------------------ | -------------------------- | ------------------------------- |
| REAL          | PLCInputFloat / PLCOutputFloat | 32-bit IEEE floating point | ±3.4 × 10^38                    |
| BOOL          | PLCInputBool / PLCOutputBool   | Single bit boolean         | true/false                      |
| INT           | PLCInputInt / PLCOutputInt     | 16-bit signed integer      | -32,768 to 32,767               |
| SINT          | PLCInputInt / PLCOutputInt     | 8-bit signed integer       | -128 to 127                     |
| DINT          | PLCInputInt / PLCOutputInt     | 32-bit signed integer      | -2,147,483,648 to 2,147,483,647 |

**Array Access Support:** Array element access is fully supported using standard Allen-Bradley array notation. Simply specify the array element in the signal's Name field, and the interface will automatically handle the array indexing:

* **Single-dimensional arrays**: `TagName[0]`, `TagName[15]`
* **Multi-dimensional arrays**: `Matrix[2,5]`, `Table[1,3,7]`
* **Program-scoped arrays**: `Program:Main.DataArray[10]`
* **UDT array members**: `Recipe[0].Temperature`, `Motors[5].Speed`

**Important Notes:**

* Boolean outputs use SINT data type in the PLC due to protocol limitations
* Array elements are treated as individual signals - no special configuration required
* String data types are not currently supported in this interface version

## Usage Examples

### Basic Setup Workflow

1. **Add Interface Component**: Create empty GameObject and add EthernetIPInterface component
2. **Configure Network Settings**: Set IP-Address to your PLC's Ethernet address (e.g., `192.168.1.42`)
3. **Set PLC Parameters**: Configure Path (`1,0` for ControlLogix), PLCType (`controllogix`), Protocol (`ab_eip`)
4. **Test Connection**: Use "Test Connect" button in the Inspector to validate configuration and verify communication
5. **Import Signals**: Use CSV import or manually create Signal child objects
6. **Runtime Operation**: Interface automatically handles read/write cycles when scene starts

### Advanced Tag Naming

**Program-Scoped Tags (Allen-Bradley):**

```
Program:MainSequence.ConveyorRunning
Program:Safety.EmergencyStop
Program:Recipe.MixingTime
```

**Array Access:**

```
ProductionData[0]    // First element
AxisPosition[2]      // Third axis position
RecipeValues[10]     // Eleventh recipe parameter
```

## Troubleshooting

### Connection Issues

**Cannot Connect to PLC:**

* Verify IP address is correct and PLC is powered on
* Check network connectivity using ping command
* Ensure Windows Firewall allows EtherNet/IP communication (port 44818)
* Verify PLC Ethernet module configuration and IP settings

**Connection Timeouts:**

* Increase Timeout value in interface properties (try 5000-10000ms)
* Check network latency and bandwidth availability
* Verify PLC is not overloaded with other communication tasks

**Path Configuration Errors:**

* For ControlLogix: Use format `1,0` where 1 is backplane, 0 is slot number
* For CompactLogix: Typically `1,0` for integrated Ethernet port
* For Micro800: Leave Path field empty
* Check physical slot configuration matches software settings

### Communication Issues

**Tags Not Reading/Writing:**

* Verify exact tag name spelling and case sensitivity
* Ensure tag exists in PLC program and is properly scoped
* Check data type compatibility between PLC tag and realvirtual signal
* Use Debug Mode to view detailed communication logs

**Manual Signal Configuration Issues:**

* **Missing OriginDataType**: Always set OriginDataType when creating signals manually (e.g., "DINT", "REAL", "BOOL")
* **Wrong Signal Component**: Ensure PLCInputInt is used for all integer types (SINT, INT, DINT)
* **Tag Name Mismatch**: The Name field must exactly match the PLC tag (case-sensitive)
* **Direction Confusion**: Remember PLCInput = Unity→PLC, PLCOutput = PLC→Unity (from PLC viewpoint)
* **Data Type Mismatch**: Verify OriginDataType matches the actual PLC tag data type in RSLogix/Studio 5000

**Slow Communication:**

* Reduce number of signals or group related signals
* Optimize PLC scan time and communication settings
* Check network bandwidth and switch configuration
* Consider increasing communication cycle time for large tag sets

**Intermittent Connection Loss:**

* Check network cable connections and switch settings
* Verify PLC Ethernet module is properly seated
* Monitor network traffic for congestion or errors
* Implement connection retry logic in critical applications

### PLC-Specific Issues

**Allen-Bradley Controllers:**

* Verify controller security settings allow external connections
* Check that EtherNet/IP services are enabled in controller properties
* Ensure sufficient controller memory for tag operations
* Validate Ethernet module firmware compatibility

**Omron Controllers:**

* Confirm EtherNet/IP adapter is properly configured
* Verify global variable accessibility settings
* Check CPU unit Ethernet port configuration

**Debug Mode Output:** When enabled, Debug Mode provides the following information in Unity Console:

* Signal initialization status with data types and connection results
* Connection error messages with detailed exception information
* PLC connection success confirmations with controller type and IP address

## See Also

* [OPC-UA Interface](/components-and-scripts/interfaces/opcua.md) - Alternative industrial communication protocol
* [S7 TCP Interface](/components-and-scripts/interfaces/s7-tcp.md) - Siemens-specific PLC communication
* [Interfaces Overview](https://github.com/game4automation/doc/blob/doc/components-and-scripts/overview.md) - Comparison of available interface options
* [Drive Component](/components-and-scripts/motion/drive.md) - Integration with motion control
* [Sensor Components](https://github.com/game4automation/doc/blob/doc/components-and-scripts/sensors/overview.md) - Integration with sensor simulation

***

© 2024 realvirtual GmbH [https://realvirtual.io](https://realvirtual.io/) - All rights reserved. No part of this publication may be reproduced, distributed, or transmitted in any form or by any means, including printing, saving, photocopying, recording, or other electronic or mechanical methods, without the prior written permission of the publisher.


---

# Agent Instructions
This documentation is published with GitBook. GitBook is the documentation platform designed so that both humans and AI agents can read, navigate, and reason over technical content effectively. Learn more at gitbook.com.

## Querying This Documentation
If you need additional information that is not directly available in this page, you can query the documentation by asking a question.

Perform an HTTP GET request on the following URL with the `ask` and `goal` query parameters:

```
GET https://doc.realvirtual.io/components-and-scripts/interfaces/ethernetip.md?ask=<question>&goal=<user_goal>
```

`ask` is the immediate question: it should be specific, self-contained, and written in natural language.
`goal` is what the user is ultimately trying to achieve, the reason they need the answer. Sharing it helps GitBook give you a better, more relevant answer. A goal is most helpful when it describes the outcome the user wants rather than restating the question. For example, with `ask=how do I create an API token`, a goal like `automate deployments from our CI pipeline` lets GitBook tailor the answer to that use case.

The response will contain a direct answer to the question and relevant excerpts and sources from the documentation.

Use this mechanism when the answer is not explicitly present in the current page, you need clarification or additional context, or you want to retrieve related documentation sections.