# Beckhoff TwinCAT

Demonstration cell including full TwinCAT3 project

## Introduction

This scene is a virtual commissioning setup for testing and validation with real or virtual Beckhoff PLCs programmed using TwinCAT. The PLC controls the process flow, including starting the robot, while the robot controller is fully simulated. It enables safe and flexible testing of automation logic without the need for real hardware. For prerequisites and setup instructions, please visit <https://doc.realvirtual.io/modellzoo>.

This document lists all signals exchanged between **realvirtual** (Unity) and a Beckhoff TwinCAT PLC for controlling the TwinCAT Demo, following the convention that **`IO.Input`** = PLC Input (from realvirtual) and **`IO.Output`** = PLC Output (from PLC). The tables below map each signal to its purpose in the modelzoo simulation.

## Prerequisites

To use the Beckhoff ModelZoo scene, you will need an installation of **Beckhoff TwinCAT 3** (recommended version: 3.1.x or higher). You can connect either a **real PLC** or use the **local TwinCAT PLC runtime (PLCSim)** on your PC.

For communication with the PLC, **TwinCAT 3 ADS** (usually part of a full TwinCAT3 installation) must be installed on the **same PC where the realvirtual.io ModelZoo is running**. Make sure TwinCAT is in **Run mode**, and that the correct **AMS NetID** and **port** are configured in the simulation settings.

We provide a complete TwinCAT project for this scene, which can be imported and compiled directly in the TwinCAT environment.

## Ready-to-Run Beckhoff Project

For this ModelZoo scene, we provide a complete **Beckhoff TwinCAT project**.\
You can import, compile, and run it directly within the TwinCAT environment to control the simulation seamlessly.

{% file src="/files/EAiZQBZ9mYt40z8cP6vL" %}

## Interface Configuration

Before connecting to a Beckhoff PLC, you need to configure the **NetID** and **Port** used for communication.

To do this:

1. Click the **Settings** icon (⚙️) in the toolbar.
2. Enter your **TwinCATInterface.NetId** and **TwinCATInterface.Port** as shown in the image below.
3. Make sure the values match your TwinCAT runtime setup.

> 📘 Refer to the official Beckhoff documentation for details on how to find or configure your **NetID** and **Port**.

<figure><img src="https://260262196-files.gitbook.io/~/files/v0/b/gitbook-x-prod.appspot.com/o/spaces%2FpYxFg97YnJX96UzNNTSd%2Fuploads%2Fgit-blob-86d5629245e896bacb93cb36633c615003b1fee8%2Fimage.png?alt=media" alt=""><figcaption></figcaption></figure>

## Signals

### 1. Robot Signals

#### 1.1 Robot Overall Status

These signals tell the PLC whether the robot is in a loading or unloading state, as determined by the realvirtual simulation.

| **Signal**                        | **Type** | **Direction**          | **Description**                                        |
| --------------------------------- | -------- | ---------------------- | ------------------------------------------------------ |
| `IO.Input.Robot.bStatusLoading`   | `BOOL`   | realvirtual → PLC (In) | Indicates that the robot is currently loading a part   |
| `IO.Input.Robot.bStatusUnloading` | `BOOL`   | realvirtual → PLC (In) | Indicates that the robot is currently unloading a part |

#### 1.2 Start Robot Programs

These signals come **from** the PLC and are used **by** realvirtual to trigger robot actions in the simulation.

| **Signal**                        | **Type** | **Direction**           | **Description**                                             |
| --------------------------------- | -------- | ----------------------- | ----------------------------------------------------------- |
| `IO.Output.Robot.bStartLoading`   | `BOOL`   | PLC → realvirtual (Out) | When set by the PLC, requests the robot to start loading.   |
| `IO.Output.Robot.bStartUnloading` | `BOOL`   | PLC → realvirtual (Out) | When set by the PLC, requests the robot to start unloading. |

***

### 2. Machine Signals

These signals handle the interaction between the simulated machine (e.g., a milling station) and the PLC.

| **Signal**                            | **Type** | **Direction**           | **Description**                                                      |
| ------------------------------------- | -------- | ----------------------- | -------------------------------------------------------------------- |
| `IO.Output.Machine.bStart`            | `BOOL`   | PLC → realvirtual (Out) | When set by the PLC, starts the machine operation in the simulation. |
| `IO.Input.Machine.bMachining`         | `BOOL`   | realvirtual → PLC (In)  | Tells the PLC that the machine is currently machining                |
| `IO.Input.Machine.bMachiningFinished` | `BOOL`   | realvirtual → PLC (In)  | Tells the PLC the machine has finished its operation                 |
| `IO.Input.Machine.bDoorOpen`          | `BOOL`   | realvirtual → PLC (In)  | Indicates the machine door is open in the simulation.                |
| `IO.Input.Machine.bDoorClosed`        | `BOOL`   | realvirtual → PLC (In)  | Indicates the machine door is closed in the simulation.              |

***

### 3. Entry and Exit Conveyor

#### 3.1 Exit Belt Signals

| **Signal**                           | **Type** | **Direction**           | **Description**                                                          |
| ------------------------------------ | -------- | ----------------------- | ------------------------------------------------------------------------ |
| `IO.Output.ExitBelt.Motor.bStart`    | `BOOL`   | PLC → realvirtual (Out) | PLC requests the simulation to start the exit conveyor motor.            |
| `IO.Input.ExitBelt.Sensor.bOccupied` | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates whether the exit belt sensor is triggered/occupied. |

#### 3.2 Entry Belt Signals

| **Signal**                            | **Type** | **Direction**           | **Description**                                                           |
| ------------------------------------- | -------- | ----------------------- | ------------------------------------------------------------------------- |
| `IO.Output.EntryBelt.Motor.bStart`    | `BOOL`   | PLC → realvirtual (Out) | PLC requests the to start the entry conveyor motor.                       |
| `IO.Input.EntryBelt.Sensor.bOccupied` | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates whether the entry belt sensor is triggered/occupied. |

***

### 4. HMI (Buttons & Lights)

These signals correspond to the simulated HMI panel. Some are set by the simulation and read by the PLC (Inputs), while others are set by the PLC and read by the simulation (Outputs).

| **Signal**                              | **Type** | **Direction**           | **Description**                                         |
| --------------------------------------- | -------- | ----------------------- | ------------------------------------------------------- |
| `IO.Input.HMI.OnSwitch.bOn`             | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates the main HMI switch is turned on.  |
| `IO.Input.HMI.Emergency.bOn`            | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates an emergency button is pressed.    |
| `IO.Input.HMI.AutomaticButton.bPressed` | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates an “Automatic” button press event. |
| `IO.Output.HMI.AutomaticButton.bLight`  | `BOOL`   | PLC → realvirtual (Out) | Turns the Lamp of the button on.                        |
| `IO.Input.HMI.Robot.bOn`                | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates the robot button is pressed.       |
| `IO.Input.HMI.EntryBelt.bOn`            | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates the entry belt button is pressed.  |
| `IO.Input.HMI.ExitBelt.bOn`             | `BOOL`   | realvirtual → PLC (In)  | Simulation indicates the exit belt button is pressed.   |
| `IO.Output.HMI.Robot.bLight`            | `BOOL`   | PLC → realvirtual (Out) | Turns the Lamp of the button on.                        |
| `IO.Output.HMI.EntryBelt.bLight`        | `BOOL`   | PLC → realvirtual (Out) | Turns the Lamp of the button on.                        |
| `IO.Output.HMI.ExitBelt.bLight`         | `BOOL`   | PLC → realvirtual (Out) | Turns the Lamp of the button on.                        |

### 5. TwinCAT Configuration

1. **Match Each Signal**\
   In your TwinCAT PLC project, create variables for every one of the signals listed here. Ensure the variable **names** match exactly (case-sensitive) and the types are all `BOOL` unless otherwise specified.
2. **Map to Physical or Virtual I/O**
   * If connected to real hardware, map these PLC variables to the corresponding digital inputs/outputs.
   * For pure simulation, keep them as internal variables in the TwinCAT PLC.
3. **Enable ADS**\
   Make sure the AMS Router and ADS settings in TwinCAT are configured so Unity/realvirtual can connect. You will need the **AMS Net ID** and **Port** in your Unity project.
4. **Configure realvirtual**
   * In Unity, locate the **TwinCATInterface** (or similar script).
   * Enter the correct ADS settings (Net ID, IP Address, Port).
   * Assign each of the “IO.Input” and “IO.Output” strings to the matching TwinCAT variable.


---

# Agent Instructions
This documentation is published with GitBook. GitBook is the documentation platform designed so that both humans and AI agents can read, navigate, and reason over technical content effectively. Learn more at gitbook.com.

## Querying This Documentation
If you need additional information that is not directly available in this page, you can query the documentation by asking a question.

Perform an HTTP GET request on the following URL with the `ask` and `goal` query parameters:

```
GET https://doc.realvirtual.io/extensions/modelzoo/beckhoff-twincat.md?ask=<question>&goal=<user_goal>
```

`ask` is the immediate question: it should be specific, self-contained, and written in natural language.
`goal` is what the user is ultimately trying to achieve, the reason they need the answer. Sharing it helps GitBook give you a better, more relevant answer. A goal is most helpful when it describes the outcome the user wants rather than restating the question. For example, with `ask=how do I create an API token`, a goal like `automate deployments from our CI pipeline` lets GitBook tailor the answer to that use case.

The response will contain a direct answer to the question and relevant excerpts and sources from the documentation.

Use this mechanism when the answer is not explicitly present in the current page, you need clarification or additional context, or you want to retrieve related documentation sections.